In DWR’s discussions with the contractor about the scope of work and schedule, it was
determined that the November 1, 2017, completion target could not be met with a design
concept that included both RCC foundation replacement and conventional reinforced-concrete
slabs and walls. Therefore, an Interim RCC Foundation Replacement Concept was developed
that restored the RCC walls, though at a lower level to allow up to 2800 m3/s (100,000 ft3/s)
as a solution for an interim period only during the 2017-2018 Winter Flood Season. The plan
was to shotcrete the inside of the RCC walls for the interim period, then remove the RCC walls
in the 2018 construction season to allow completion of the reinforced-concrete slabs and walls
as originally designed, as shown in Fig. 6.
Figure 6 - Interim RCC Foundation Replacement Concept
The characteristics of the Interim RCC Foundation Replacement Concept are provided
below:
RCC is used as the foundation replacement material from Station 28+35 to 39+00.
A minimum RCC thickness of 1.5 meters (5 feet) perpendicular to the chute slope is
provided in the RCC area of the FCO Spillway chute (Sta. 28+35 to 39+00).
The RCC foundation replacement is placed in horizontal layers below the planned final
4:1 finished grade of the reinforced-concrete spillway chute, creating a roughed-in 4:1
slope for the chute.
A final 30 cm (12 inch) thick layer of RCC would be placed monolithically on a 4:1 slope
using a higher-strength enriched RCC mix to provide a durable surface for the 2017-
2018 Winter Flood Season, leaving the final RCC chute surface about 0.91 meter (3
feet) lower than the planned finished reinforced-concrete slab chute grade.
At the upper end of the RCC (Sta. 28+35), a vertical 0.91-meter (3-foot) step from the
FCO Spillway update chute finished reinforced concrete surface to the downstream
RCC surface would be used as an aeration ramp with a vertical chimney section at
each abutment to allow air to be incorporated into future flows.
At the lower end of the RCC (Sta. 38+00 to 39+00), a 30.5 meter (100-foot) long
transition section would slowly bring the RCC chute surface up flush with the finished
FCO Spillway lower chute reinforced-concrete surface.
Shorter 4.9 meter (16-foot) high RCC walls would be constructed with a similar design
as the initial concept - a vertical inside face, 4 meters (12.5 feet) across the top and
1:1 side slopes on the outside faces], which is designed to accommodate a design flow
of 2,800 m3/s (100,000 ft3/s).
A minimum of 6 inches of the inner wall face would be constructed using reinforced
shotcrete to provide a durable surface for the 2017-2018 Winter Flood Season.
94
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik