Seite - 164 - in Book of Full Papers - Symposium Hydro Engineering
Bild der Seite - 164 -
Text der Seite - 164 -
crest structure and the absence of erosion protection downstream of the crest
structures may have also contributed to the development of the erosion.
5. WHY THE INCIDENT HAPPENED
The February 2017 Oroville Dam spillway incident was the result of
interactions of numerous physical and human factors, beginning with the design of
the project and continuing during the nearly half-century until the incident. The
incident was generally the result of a long-term systemic failure of DWR, regulatory,
and general industry practices to recognize and properly address the deficiencies
and warning signs which preceded the incident. There was no one root cause, nor
can the incident reasonably be “blamed” mainly on any one individual, group, or
organization.
5.1. SERVICE SPILLWAY
The conditions that led to the service spillway chute failure have their roots
in the original design and construction of the chute, which, combined with the
locally poor geologic conditions at the site, resulted in vulnerabilities in the as-built
structure. These vulnerabilities were not recognized in various inspections and
evaluations that were completed throughout the history of the structure. In fact,
warning signs of the vulnerabilities came to be accepted as “normal,” and then
generally were not questioned further. Because the seriousness of the
vulnerabilities was never recognized, chute slab repair efforts were neither well-
conceived nor effective, and likely contributed to the deterioration of chute
conditions over time.
As detailed in the forensic investigation report [1], the spillway chute design
was generally at the middle of the range of practice for the 1960s for spillway
chutes founded on rock. For a structure of the significance of Oroville Dam, the IFT
would expect the design to have reflected the best practices of the time, which it
did not. The one aspect in which the design was at the very low end of practice of
the time was the significant protrusion of the chute underdrains into the slab
section. This feature was uncommon and led to the development of extensive
cracking over the drains and resulting leakage through the slab at the cracks.
Communication among geologists, designers, and construction managers
during the service spillway’s design and construction apparently was poor. This
ultimately resulted in a design which was probably more appropriate for a spillway
chute on rock foundations rather than one constructed on more variable foundation
conditions, including strongly weathered rock, most notably an extensive area of
such material at the location of the initial chute slab failure. These conditions
164
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik