breaker to preserve the true free length even when surrounded by grout. In this
case, the load is still maintained by the gripping wedges in the head (in the case
of strands), or by the lock nut (in the case of bars), and attempts to expose such
heads, or indeed to attempt, somehow, a lift-off test, would be inviting trouble.
Fourthly, strain gages or load cells of adequate reliability were simply not
available to provide long-term monitoring capability, and indeed are still not
available today. Compounding this issue is the stark fact that there is still no
completely reliable, calibrated NDT Method that can be used to check the
residual load, or the integrity, of wire or strand tendons, fully grouted or
otherwise. It may be noted, however, that some recent methods are showing
promise for bar tendon assessments.
Fifthly, contemporary construction records may not always be available for
review and, even if they are, they may not contain vital pieces of information, the
clues to the likely adequacy of the construction details to preventing long-term
corrosion. A case in point here would be the static (bleed) and dynamic
(pressure filtration coefficient) stability properties of the grouts: if either property
were deficient, then bleed pockets would develop, especially in the tightly
arranged “bundles” of wires so common in early legacy anchors.
Sixthly, it is not uncommon for Owners to consider somehow exhuming
production anchors and then closely examining the tendon for signs of corrosion.
Exhumation is feasible if the dam is being deconstructed for decommissioning.
This is a relatively rare occurrence and of course is not an option for evaluating
legacy anchors in dams required for extended, long-term service. Alternatively, it
is technically feasible – if sufficient access exists to allow for the mobilization of a
major piece of drilling equipment – to overcore the entire anchor and remove it for
inspection. However, this is a very difficult and typically costly option since the
drilling method must be precisely colinear with the anchor, and the tendon will not
permit the anchor to be removed in convenient “runs,” for example, of 1.5 or
3.0 m. Furthermore, the grout is typically damaged or lost in the drilling process,
and the concern will remain if the particular anchor removed is actually
representative in its condition of the others, or if any localized corrosion-induced
damage will indeed be recognized.
As a final point, it is easy to be critical of the contemporary standards used
in the design and construction of legacy anchors. However, at the time of their
installation, design lives of 25-30 years were considered satisfactory, whereas
some of these installations are now over 50 years old. “Modern” anchors (with
Type I Corrosion Protection) are children of the late 1990’s, and a great deal of
knowledge has been accumulated since then fuelled, in part, by our current
attitudes to risk assessment such as inherent in the Potential Failure Modes
Analysis process.
4. KEY FACTORS IN RISK EVALUATION DURING A PORTFOLIO RISK
ASSESSMENT PROCESS
In the case where an Owner is responsible for a number of projects
dependent for stability on prestressed rock anchors, it is logical and essential to
conduct a preliminary screening process to identify and prioritize the most
worrisome projects. This is akin to the process first adopted by the U.S. Army
708
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik