and the average absolute percentage difference (AAPD) is about 8.8%. For downstream slope, (AME) is about
0.075 and (AAPD) is about 4.1% which are all within the acceptable accuracy.
Table (1): Minimum calculation results of factor of safety
F.S downstream slope
F.S upstream slope
Methods of calculation Steady state
End of
construction
End of
construction
Rapid
drawdown
1.90
1.911
2.25
1.618
Present study
GeoStudio software (Bishop's)
1.80
1.86
2.03
1.515
Referance [21]
Analatical solution (Bishop's)
5.56%
2.47%
10.83%
6.79%
Absolute percent difference
7. Application of Geostudio on Mandali Dam
Mandali dam is an earth fill dam which is located on Harran Wadi, in the governorate of Diyala which is
extends to the northeast of Baghdad, Iraq (Fig.5). The dam has been designed by Directorate General of Dam and
Reservoirs, Iraq. The Wadi bed is gravely and permeable to some depths as it is clear from the geological
investigations Mandali dam has a central core and the dam total length is about 1316 m. The maximum height of
the dam is about 14m [Ministry of water Resources, Iraq] [22]. Figure (6) shows the dam cross-section, while
Table (2) gives the material properties of the dam components. The dam geometrical properties can be seen in
Table (3).
Table (2): Material properties of Mandali dam, Iraq [22, 23].
Layer (soil type)
Physical and
mechanical properties Shell
(Sandy soil) Clay core
(Very stiff
clay) Foundation
(Stiff clay) Filter
(Sandy
gravel soil)
Bulk density (γ) [KPa] 21 19.2 22 21
Angle of internal friction (ϕ) [degree] 40 15 30 37
Cohesion (c) [KPa] 0.0 40 5 0.0
Permeability (k) [m/sec] 1.37*10−5 9.88*10−9 10−8 10−2
Poisonʹs ratio (ν) 0.3 0.36 0.32 0.4
The elastic Modulus (E) [KPa] 35000 19000 100000 30000
7.1 Safety Criteria of Mandali Dam
The Geometric properties of Mandali dam were checked using BDS (1994) [19]. Table (3) gives the
results of the comparison. It can be noticed that the geometric design of the dam is acceptable based on the
recommendations of The British Dam Society (1994) [19].
Table (3): Comparison between original section of Mandali dam and (BDS) safety limits
Parameter Mandali
Dam (BDS) Safety limits Safety of dam status
Crest width 8.0 m Not less than 2.0 m Acceptable
Upstream slope 2.7:1 2.5:1 Acceptable
Downstream slope 2.4:1 2:1 Acceptable
Free board 1.50 m Min. free board = 1.50 m at Max.
Fitch = 4 km. Acceptable (Maximum head over
spillway = 2.5 m)
Bed width of core 58 m Not less than 𝐻
3 = (4.67 m) Acceptable
Core slope 1:1.77 1:12 Acceptable
1201
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik