REFERENCES
[1] DOHWA ENGINEERING CORPORATION. Design report for functional
recovery of seepage measuring facility of the upper dam of Cheongpyeong
Pumped Storage Power Plant , 2016.
[2] KOREA WATER RESOURCES ASSOCIATION. Dam design criteria, 2005.
SUMMARY
This study intends to find out the possibility of recovering the original
function of the dam by analyzing the cause of functional degradation of the
seepage measurement facility that may occur in old dams. The dam concerned is
the upper dam of Cheongpyeong Pumped Storage Power Plant constructed in
1980, which is approximately 35 years ago, and it was not possible to measure
the leakage except during the period of localized heavy rain as the water was not
collected in the seepage measuring facility installed in the downstream area of
the dam
Various field investigations were conducted to determine the cause of
functional degradation of the seepage measuring facility. According to the result
of naked eye investigation, the measuring facility did not have significant
problems in carrying out its functions. Two points on both banks of the collecting
wall were excavated to confirm the groundwater leakage around the water-
collecting wall and it confirmed the leakage of groundwater in the foundation of
the collecting wall in the right bank area of the dam. The result of strength
measurement to confirm the soundness of the concrete of the collecting wall
indicated that the condition of the wall is acceptable. In addition, a boring
investigation was carried out to determine the geology of the foundation ground,
and the Lugeon test, which was conducted to determine the permeability through
the collecting wall and foundation soil, showed the sections with high lugeon
values.
The comprehensive analysis of the investigation results showed various
paths through which the leaking water flowed instead of being collected in the
collecting wall and came to the following conclusions. First, the foundation of the
water-collecting wall is located above the soft rock layer which is the bedrock.
The quality of this soft rock layer is poor with the developments of cracks and
joints and this layer displays 3Lu or greater permeabilty in all sections, which
identifies the soft rock layer as the major seepage pathway. Second, the
investigation found the leakage of groundwater noticeable by the naked eye in
the contact area between the concrete of the foundation of the water-collecting
wall and the bedrock and identified the leakage in the contact area as another
major cause. Third, the condition of the concrete of the collecting wall was
relatively acceptable. However, the Lugeon test showed that the lugeon value
1807
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz