lead up to the top of next RCC lift. After placement of the 3 m thick RCC lift, the
top 5 m stage was grouted. Subsequently, the holes for the next 3 m lift were drilled.
Although the consolidation grouting was conducted, the important lesson learnt
from this procedure was that the drilling and grouting process of the 3 m high
abutments needed at least 5 to 7 days, which forced the RCC placement for the
3m lift in a total 6 to 8 days or more, which considerably hold back the construction
progress of the RCC dam. Moreover, grout was found to leak out of the rock
surfaces during the grouting due to the high grouting pressure, which required
immediately and effectively plugging or caulking.
The dam has a grouting/drainage gallery at El. 634.0 m near the dam heel
and two control galleries at El. 675.0 and 720.0 m, respectively. Both sides of the
galleries extended into rock in due lengths as grouting/drainage adits. On both
sides of dam crest, the grouting/drainage adits were excavated. The galleries are
accessible through a vertical stairway shaft in the middle pier of the dam, and from
the downstream slopes. Two lines of grout curtains were implemented from the
grouting/drainage gallery and adits. The main curtain grout holes are inclined
arranged to the upstream with an angle of 5° to vertical in a spacing of 2.0 m, while
the auxiliary curtain grout holes (also 2.0 m spacing) downstream of the main
curtain are vertical. The hole depth is 74 m down into rock at dam bottom El. 634 m,
decreased to 43 m at the crest level at El. 763.0 m. On downstream side of the
grout curtains, a line of drainage holes of 110 mm diameter and 3.0 m spacing was
drilled from the grouting/drainage gallery and adits inclined to downstream with an
angle of 5° to vertical.
5.2. UPSTREAM BLANKET
The upstream cofferdam is a rock fill embankment of 41 m height and 82 m
length at crest El. 676 m with an upstream sloping core, located at 85 m to the
main dam axis. The cofferdam is 8 m wide at the top with 1V : 2.5H slope on
upstream and 1V : 1.75H slope on the downstream surface. The thickness of the
sloping clay core is 5 m at top and 17 m at bottom, protected by a layer of 0.4 m
thick riprap and 0.6-m thick dry-stone pitching. Beneath the sloping core, a filter
layer is placed which is inclined to upstream at an upper and lower slope of
1V : 1.7H and 1V : 1.5H, respectively. The cofferdam is seated on the rock
foundation. Because the abutments are steep and the limestone rock mass is well
developed in joints, fissures, the clay core is widened in the areas contiguous to
the interfaces between the clay core and abutment flanks by 20% of its respective
thickness at that level.
In order to additionally enhance the sealing effect of the dam foundation, the
upstream cofferdam was utilized. The cofferdam was partially removed to a level
below El. 670.0 m. After the space between the main dam and upstream cofferdam
was filled and compacted with soil, an impervious blanket was placed on the filled
soil from the upstream face of main dam extending to the sloping imperious clay
1898
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik