Seite - 1934 - in Book of Full Papers - Symposium Hydro Engineering
Bild der Seite - 1934 -
Text der Seite - 1934 -
1. For embankment dams of similar height, the maximum foundations
stresses are similar except for the stress bulb width.
2. A 1:1.5 upstream and downstream sloped rockfill dam imposes less
foundation stresses than a flatter 1:2.0 sloped rockfill dam. This observation
is very important as widening the width of an embankment dam with flatter
slopes does not necessarily provide increased safety nor economy.
3. For the rockfill part of a composite dam the most steeper slopes that provide
the required safety margins is adequate and thus must be selected. The
foundation improvement will thus be required over a smaller foot-print and
the cost savings can be used to provide treatment even deeper that is
beneficial.
4. The incremental stresses imposed by even a large dam on the foundation
decreases rapidly with depth, with minimal stress increase beyond depths
exceeding 15 to 20% of the dam height. The most important zone for
consolidation is thus the upper most foundation layers within this impacted
depth.
5. RCC dam and/or spillway blocks on weaker foundations are also normally
provided an upstream slope partially or for the full height of the dam.
In traditional dam construction, how consolidation grouting is undertaken
still remains less effective as it is normally done after exposing the foundation
but prior to commencing dam construction. For very week dam foundations
such an approach is not beneficial particularly in zones where a concrete or
RCC spillway section needs to be placed. In such areas, it would be more
effective if a confining concrete or RCC cap layer, several meters in thickness
be placed first and then followed with consolidation grouting. If this confining
layer is in mass concrete pipes can be left in place to minimize subsequent
drilling for consolidation grouting. Proper consolidation grouting enhances
curtain grouting for sealing the foundation for water tightness. This also allows
higher grouting pressure such as at the foundation-dam interface where it
matters most. Such construction requirements should be put in place at the
time of tender.
Irrespective of dam type, proper drainage downstream of the grout
curtain is critical for the safety of the dam. Thus the placement of the grouting
gallery is also of importance. Usually upstream of the grouting gallery the intent
of the consolidation grouting is for both water tightness as well as for
strengthening the foundation whereas on the downstream part more emphasis
shall be on foundation strengthening. The curtain grout must follow a single
axis through the composite dam to be most effective as well as for economic
considerations.
1934
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik