2.2. TENDER DESIGN
The proposed works involved extensive grouting of the upstream face of ten
blocks in Cathaleen’s Fall Dam, i.e. Blocks M to V. Grouting had to be carried out
in stages, with each of the existing horizontal construction joints, as well as any
voids, being treated. Water pressure tests had to be carried out in boreholes during
the course of the works to monitor the adequacy of the grouting. Permanent
drainage holes had also be provided to reduce the adverse effects of any remaining
or future seepage.
2.2.1. Grout Holes
The grout holes in the inspection gallery had to have a minimum diameter of
46 mm and a maximum diameter of 72 mm with depths up to 10 m in downward
direction and depths up to 5 m in upward direction. The grout holes on the crest
had a depth up to 20 m in downward direction. The grouting sequence of the
downward drill holes was bottom-up with ordinary portland cement or microfine
cement. The packer had to be raised in a way, so that the packer is always midway
between the joints. The primary grout holes were spaced at 2 m, and the secondary
grouting holes 2 m between the primary holes, so that there is one hole every
meter.
2.2.2. Requirements for Equipment
The drill rigs had to be of a suitable size for use on the crest and particularly
in the confined space of the inspection gallery. The inspection gallery was 1.2 m
wide and between 1.75 m and 2.1 m high and no widening of or cutting out of
recesses in the gallery walls were permitted. The drilling method had to provide
accurate results for judgement of the actual conditions in the dam – structural
condition of in-situ concrete, cracks, joints, voids, porosity as well as the actual
uplift pressure.
2.2.3. Requirements for Grouting Works
Since the dam had to remain in operation during the sealing works, high
demands on grouting works were set. The flow rate had to be kept low – under
normal circumstances well below 2 ltr/min. The maximum grouting pressures were
limited as follows:
from crest (35.36 m O.D.) to 29.5 m O.D.: 3 bar
below elevation 22.0 m O.D.: 5 bar for cementitious materials and
4 bar for synthetic resins
for elevations between 29.5 m O.D. and 22.0 m O.D.: the allowable
maximum pressures had to be interpolated
1997
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik