Seite - 2162 - in Book of Full Papers - Symposium Hydro Engineering
Bild der Seite - 2162 -
Text der Seite - 2162 -
The investigated load cases are shown in Table 1 below. Since the
geometry is completely symmetric, it was not necessary to simulate all
combinations, so we concentrated on the operation of unit 1.
Table 1
Investigated load cases
OP Penstock 1(Side) Penstock 2(Middle) Penstock 3(Side)
1 100% 100% 100%
2 100% - -
3 100% 100% -
4 100% - 100%
Because in the previous investigation of the measurements it was found
that the reason for the oscillations is the pressure drop, the variation of the total
pressure between inlet and outlet is examined. This is done for different load
cases.
4.2. LOAD CASE 1
This load case corresponds to the measurement data. In Fig. 10 below, the
total pressure differences are shown.
For the reference geometry in the left and right penstock, oscillations of
pressure differences of approximately 70 kPa can be observed. This corresponds
quite well to the value of measurements even when the amplitude in the
simulation is smaller. This can be explained because in strong swirling water
flows, the simulation usually under-predicts the swirl intensity.
As a consequence, the losses caused by the swirl component are under-
predicted as well. However, it is obvious that the original geometry pressure
vibrations exist, which would lead to power oscillations.
Fig. 10
Total pressure difference between inlet and outlet cross-sections, load case 1
2162
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik