series separately (see figure 4). Spacing of A and B series were 3 meters.
Pressure for contact grouting in FLA panel increased up to 7 bars due to concrete
lining bearing. Water cement ratio of grout is 0.8 by weight.
B: pattern of secondary holes
A: pattern of initial holes
Fig. 4
Contact Grout Holes Arrangment
4.3 COMPARING OF ISA AND FLA PANELS GROUTING PROCESS
Although drilling of borehole in ISA panel could be done faster and lower
cost also does not delay the project schedule, but due to technical limitations in
applying the injection pressure, satisfied results of grout penetration inside the
gaps and sacks h not achieved. Inspection of core samples indicate that the
grout penetration in the voids is not desirable and the pumice pieces were not
consolidated predominantly (see figure 5-a).
In FLA panel, injection pressure up to 7 bars were possible, so the
penetration of grout in the voids were acceptable. As a result, injection in the FLA
panel were get the pumice pieces and cement parts integrated, and solidified in
the cores mostly (figure 5-b).
B: Core sample of FLA panel
A: Core sample of ISA panel
Fig. 5
Core Samples from ISA and FLA Panels
2187
Book of Full Papers
Symposium Hydro Engineering
- Titel
- Book of Full Papers
- Untertitel
- Symposium Hydro Engineering
- Autor
- Gerald Zenz
- Verlag
- Verlag der Technischen Universität Graz
- Ort
- Graz
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Abmessungen
- 20.9 x 29.6 cm
- Seiten
- 2724
- Schlagwörter
- Hydro, Engineering, Climate Changes
- Kategorien
- International
- Naturwissenschaften Physik
- Technik