6.4 FrequencyWeighting 51
Ifweweight this process transfer function byW(s)=1/(s+1), then the new
system becomesWG=10/(s+10). Now, the gain declines with increasing fre-
quency, fromamaximumofoneat zero frequency toaminimumofzeroat infinite
frequency.
Byweighting the original system,G, by theweighting function,W, we cause
theH2 normof the combined system,WG, to be relativelymore sensitive to low-
frequency disturbances.Whenwedesign a controller byminimizing theH2 norm
associatedwithWG,wewill typicallyfinda system that is better at rejecting low-
frequency loaddisturbances thanadesignminimizing theH2 normassociatedwith
G. For the weighted system, optimization will avoid controllers that reject high-
frequencyloaddisturbances,becausetheweightedsystemalreadyrejectsthosehigh-
frequency inputs.
Roughly speaking, a weighting function instructs the optimization method to
reducethegainandsensitivityforcertainfrequenciesandtoignorethegainforother
frequencies.Theweighting functionsdonot alter the actual system.Theweighting
functionsareonlyusedtoalter thecost functionandoptimizationmethodthatdeter-
mine theoptimal controller.
Figure6.4 shows the regulation feedback system of Fig.6.1 with additional
weightingsforthedisturbanceandnoiseinputs.Theweightingsmodifythefoursys-
tem transfer functions andassociated sensitivities inEq. 6.2 tobeWdGud,WdGηd,
WnGun, andWnGηn.Thecost function inEq.6.5becomes
J =μ2||WdT||22+μ2ρ2||WdPS||22
+||WnCS||22+ρ2||WnT||22. (6.9)
Consider an example in which we begin with the process, P, in Eq. 6.8. To
emphasize low-frequency loaddisturbances, setWd =1/(s+0.1) tobea low-pass
filter.Thatweightingfiltersoutdisturbances that are significantlygreater thanω=
0.1.Toemphasizehigh-frequencysensornoise,setWn = s/(s+10).Thatweighting
filters out noise that is significantly less thanω=10. By using these two filters,
the optimization method puts very low weight on any disturbances in midrange
frequenciesofω= (0.1,10).
n
P
d
C
u y n
Wd
d
~
Wn ~
Fig.6.4 Basic regulationfeedback loop inFig.6.1withadditionalweightings fordisturbanceand
noise inputs. Theweightings alter the cost function to emphasize particular frequency bands for
disturbanceandnoise,yieldingamodifiedoptimal controller
Control Theory Tutorial
Basic Concepts Illustrated by Software Examples
- Titel
- Control Theory Tutorial
- Untertitel
- Basic Concepts Illustrated by Software Examples
- Autor
- Steven A. Frank
- Verlag
- Springer Open
- Ort
- Irvine
- Datum
- 2018
- Sprache
- englisch
- Lizenz
- CC BY 4.0
- ISBN
- 978-3-319-91706-1
- Abmessungen
- 15.5 x 23.5 cm
- Seiten
- 114
- Schlagwörter
- Control Theory --- Engineering Design Tradeoffs, Robust Control, Feedback Control Systems, Wolfram
- Kategorie
- Informatik