headworks structure would need to remain in place [3]. However, for the design
team and dam safety regulators to be comfortable with this situation, many
explorations were performed within the upper chute to better understand the actual
thicknesses and quality of the concrete slabs, foundation rock quality, concrete-
foundation interface conditions, and so on.
To address design concerns, the chute slab concrete was cored at 68
exploration points within the upper half of the FCO Spillway chute, upslope from
the initial scour hole. Of the 68 locations, 24 were additionally cored into the
foundation rock to assess foundation rock conditions. Falling-head permeability
tests were completed in 18 locations to test the bond between the slab concrete
and the foundation rock. Ground-penetrating radar (GPR) was also used to image
the concrete and the underlying foundation rock in the upper chute; the results from
the GPR imaging were used to guide some of the physical exploration locations.
Eight wireless vibrating-wire piezometers were installed in six locations to
determine groundwater pore pressures beneath the chute slab during spilling and
non-spilling events.
In addition to explorations to address design concerns, DWR performed
forensic studies that aimed to address the following potential physical factors
raised by the Independent Forensic Team in their preliminary report [10]: 1)
thickness of the chute slab above herringbone underdrains; 2) variations in slab
thickness, 3) characteristics of weathered foundation rock and intensely-weathered
rock; 4) foundation rock bonding with the concrete slab; 5) effects of extended
drought impacts on foundation materials; and 6) groundwater pressures exerted
on the chute slab.
Four areas of the undamaged concrete-lined FCO Spillway chute were
evaluated using saw-cut trenching to examine the foundation conditions and
potential physical factors that might have contributed to the damage of the FCO
Spillway chute. Each area of the saw-cut concrete chute was carefully lifted away
from the surrounding slab concrete to minimize disturbance. Each location was
then photographed in detail prior to performing any investigative work. Once the
area was thoroughly documented, the gravel surrounding the perforated
underdrain pipes (vitrified clay pipes placed during original construction) was hand-
picked from around the pipes. Any non-rock materials mantling the foundation rock,
such original excavation debris, were measured, sampled, described, and then
cleared off for final geologic mapping of the foundation rock surface.
The findings from the FCO Spillway chute explorations indicated that – where
measured – the concrete slab was greater than 18.3 cm (7.2 in) thick above the
underdrain pipes; the concrete slab thickness varied from about 38 cm (15 in) to
over 2.1 m (7 ft); there were not large extents of intensely-weathered to
decomposed rock; there was generally good bonding between the rock and the
concrete slab; and groundwater piezometric pressures within the chute’s
foundation rock were typically below the concrete-foundation interface.
113
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik