2.2.4 Corrosion and Corrosion Protection
References [1] and [2] provide an analysis of the PTI Recommendations to
that point (i.e., including the 2004 version) and a summary of over 400 individual
case histories. Note that the provisions of the PTI 2014 edition are sensibly the
same as in 2004, while the database has recently been further updated [3]. It is
extremely important in the context of legacy anchors to gain perspective of
contemporary attitudes, and the development of these attitudes with time.
In summary, the anchor grout itself was regarded, during the early decades
of practice, as an acceptable barrier to corrosion, for both the bond and free
lengths. It was only with the 1996 version of the PTI Recommendations that full-
length protection by at least one plastic sheath was required for permanent
anchors, i.e., Class I protection, so matching contemporary standards of care in
Europe (Figure 1).
3. CHALLENGES TO EVALUATING LEGACY ANCHORS
There are many challenges relating to the design and the construction of
such anchors, and to practical/logistical aspects of condition assessment. These
challenges are common to dam Owners and Regulators throughout the dam
anchor world.
Firstly, it is clear that the majority of dam Owners and their consultants
simply did not contemplate at the time of design and construction that long-term
monitoring would be advantageous, let alone fundamental to risk management.
The general philosophy was that anchors designed and constructed to the
standards of the day would not corrode since the steel would be encased in
grout, and placed into boreholes whose immediate proximity was pregrouted (to
prevent water ingress and to prevent anchor grout loss). The anchor head itself
was generally encased in concrete. Further, in acknowledgement that the tendon
would naturally suffer long-term stress loss (principally due to relaxation), the
post-tensioning specialists selected Lock-Off/Transfer Loads, which included an
allowance for these losses, the magnitude and rate of which were well known
from structural post-tensioning projects. Such elevated tendon stress levels,
while (usually) still within the elastic response range (i.e., ≤ 80% fpu), would
however increase the tendency for stress-induced corrosion to be initiated or
accelerated under certain conditions. No provisions were made for installing
restressable anchor heads.
Secondly, it was exactly these old methods which have now rendered lift-off
testing unfeasible: without a developed free length, it is impossible to directly
measure the residual load in the tendon, or to determine its distribution within the
free length or, of course, the bond length.
Thirdly, it is often the case that the anchor heads are, for all practical
purposes, inaccessible for any type of inspection or testing. In some cases, the
functional anchor heads could be rendered accessible, but there would be a
natural reticence to “probe too deeply” for fear of disturbing the anchor head –
not so much from a load holding viewpoint, as the tendon is fully bonded below,
but from the corrosion protection viewpoint. This is particularly the case with
legacy anchors which do feature a greased and sheathed coating as a bond
707
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik