Page - 1117 - in Book of Full Papers - Symposium Hydro Engineering
Image of the Page - 1117 -
Text of the Page - 1117 -
3.4. SAFETY-CRITICAL APPURTENANT STRUCTURES AND CONTROL TECHNOLOGY
The aim is to assess the reliability of the weir gate’s control technology under
unusual and extreme conditions. In a run-of-river plant the functionality of the weir
gate is of vital importance to avoid overtopping the weir and overflowing of the river
banks upstream of the weir.
This chapter of the safety assessment describes the control technology of
the weir gates, which is under normal conditions fully automated to maintain the
head water at the concessionary level. In case of failure of the automatic control
and concurrent rising of the headwater level, a backup control system is taking
over to open the weir and avoid overflowing. As an alternative or if the backup
system should fail, the weir can be operated manually from the control room in the
powerhouse or from a separate control station at the weir site.
Both plants have a power supply from their own production. In case of failure
of the internal power supply, it can be switched to external supply or supply from
the emergency diesel generator.
The outcomes from the seismic safety assessment demonstrated that the
weir structure and powerhouse, which house the hydraulic system, will remain
intact. The hydraulic system is therefore with high probability operable also after
an earthquake has occurred. In case of failure of the hydraulic aggregate, in
Ruppoldingen a fix installed backup aggregate is available. In both plants, a mobile
emergency aggregate with its own diesel generator is available. This allows
opening of one gate at the time.
Regular trial runs of the backup systems including moving of the gates with
the help of these systems ensures that for both plants, the equipment is well
maintained and the personnel is well trained to use the equipment even in
emergency situations. The assessment could conclude that sufficient redundancy
is available to safely open the weir gates also under unusual and extreme
conditions.
3.5. STRUCTURAL SAFETY ASSESSMENT
In this chapter, the safety of all water-retaining structures, i.e. weir, gates and
powerhouse are quantitatively assessed. This requires verification of structural
stability (sliding, overturning and buoyancy), structural and foundation stress
analyses and behavior against reviewed operational and hazard scenarios (load
cases). Head and tailwater levels for the same load cases considered at the time
of design were updated based on latest hydrological data. The post-earthquake
functionality of the gates needs also to be verified.
1117
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik