Fig.7
2017/7/25 Temperature data comparison between optical fiber and digital
thermometer in 7#11
Fig.8
2017/8/4 Temperature data comparison between optical fiber and digital
thermometer in 7#11
From Fig.7 and 8, optical fiber temperature measurement data and digital
thermometer temperature data are different, but the difference is small. The
relative error is within 1 ℃ between the two methods. Therefore, the optical fiber
temperature measurement can meet the engineering requirements.
4.2. VARIATION OF TEMPERATURE INSIDE CONCRETE AT EARLY AGE
Taking the unit 7 # 11 of Wudongde Dam as an example, the temperature
Variation is analyzed with age at the starting point at downstream surface and the
end point at upstream surface(Fig.9).
During the construction period, the temperature of the dam is controlled by
the cooling water. In order to facilitate the expansion of transverse joint, the cooling
time is generally 2 to 3 days after the placement. Therefore, the change of concrete
temperature is the result of the combined effect of hydration heat and cooling
water. T/(℃)
Tim e(2017/7/25)
T/(℃)
Tim e(2017/8/4)
1430
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik