• Maximum elapsed time from introduction of water to the mix and final
compaction is 60 minutes.
Lift Joint Conditions: The thickness of the layer shall not exceed 300 mm,
and shall be aggressively cleaned before applying bedding mortar and placing
next layer. Good lift joint conditions are a vital component of good RCC
construction. The underlying goal is to place subsequent RCC lifts before the
underlying lift has set, allowing the lifts to bond to each other. Cleaning shall
include removal of all loose material, cement paste, fine particles, still and current
waters, snow, ice, oil and grease and other detrimental materials. In particular,
the surfaces of joints shall be kept free of dust at all times. All horizontal joints
shall be prepared for the next lift by removing mortar coating, laitance, or other
contaminants by water jet or other approved methods. After this initial
preparation, the surface shall be kept damp until receiving the bedding mortar
application prior to the next RCC placement.
Bedding Mortar: A lift surface is considered a "cold joint" if the surface is
damaged by weather or equipment, frozen, Cold joint treatment consists of
thorough cleaning of the surface and placement of a layer of bedding mix
concrete (bedding mortar) immediately prior to placement of the successive RCC
lift. Not more than 15 minutes shall have elapsed after spreading the bedding
mortar when RCC is spread on it. Figure 4 shows cleaning of lift Surface and
spreading of bedding mortar.
Fig. 4
Cleaning of Surface and spreading of bedding mortar (Uma Oya Project)
4.3. COMPACTION AND VERIFICATION
Compaction is generally viewed as one of the most important elements in
RCC Construction. During construction of the RCC, adequate compaction will
have one of the most profound impacts on the quality of the finished RCC dam.
In RCC dams, the in-place compaction and water content of the RCC in the
lifts are tested using nuclear gauges in accordance with ASTM C1040 and ASTM
D1557. The testing shall be performed frequently; Acceptance criteria for in-place
density of the RCC require no test less than 98 percent of required compaction.
The variation of moisture outside minus 5% and plus 5% of the optimum moisture
content shall require aggregate moisture contents testing and control of water
contents at the batch plant. Re-compaction of the RCC shall not be allowed
1511
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik