Apparent Lugeon Values, however, as the authors have observed on a major
recent project in the Pacific North West. Water testing of the final hole series and
verification holes should always be performed to prove the residual permeability
of the treated rock mass.
2.6. ALLOWABLE SAFE INJECTION PRESSURES
A prime rule in any remediation is “First – Do No Harm,” and this is a logical
and proper dictum to which the authors fully subscribe. However, the whole
issue of safe rock grouting pressures under existing dams has reached levels of
hysteria, especially in uninformed and inexperienced circles. Bearing in mind that
a) a dam foundation is a 3D structure, b) contemporary computer-aided grouting
control and recording systems provide essentially continuous real-time
pressure/rate of injection data for each stage, and c) QA/QC programs are
generally now quite sophisticated, then the authors believe that the highest safe
injection pressures should be used, for both economic and technical reasons.
“Rules of Thumb” (e.g., 1 psi/foot) can be discarded provided proper and
progressive testing is conducted, and all processes are carefully controlled and
monitored during injection.
2.7. JOINT INSTRUMENTATION MONITORING PLANS AND LONG-TERM
PERFORMANCE MONITORING
It is normally the case that the dam to be remediated will already have
some amount of instrumentation in its body and in its foundation. (It is usually the
case that the results of this instrumentation will have highlighted the actual need
for remediation, in concert with visual observations.) Further instrumentation
should be added just before or during the grouting, to target specific “problem
areas,” or simply to ensure a broad coverage without data gaps. The result is a
plethora of instruments, typically now configured to provide data in real time.
It is essential for Dam Safety Assurance during construction that the Owner
and the Contractor partner to collect, study and act upon these data in real time,
regardless of whose contractual responsibility or liability it may be to do so. The
most efficient strategy is to create, prior to construction having commenced, a
Joint Instrumentation Monitoring Plan (JIMP). This will identify which instruments
are to be read, by whom, and at what frequency. The JIMP will also provide
Threshold and Action Level guidance for each instrument, and identify courses of
action when these levels are reached.
We also note that a JIMP is implemented most effectively when the Owner
and the Contractor can view the data while being physically in a joint “Mission
Control” facility. In this way, the impact of the Contractor’s work on the dam and
its foundation can be seen in real time, and acted upon accordingly when
necessary.
1619
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik