check as the height of the locations are relatively high among the sections where
water-collecting walls are installed (Fig. 5).
Fig. 5
Position of Test Pit Investigation
The NPT-1 test pit investigation was conducted at the corners of the water-
collecting wall in the right bank of the dam. The groundwater was flowing into the
excavation surface from 4.5m below the surface and the excavation could
continue down to 4.8m below the surface. The mixture of buried layers (silty
gravel layer mixed with sand) and boulder stones was distributed down to 1.5m
below the surface of the ground. Concrete water-collecting wall (3m high) is
installed at the bottom of the buried layer. There was no damage or leakage such
as cracks and breakage on the concrete of the collecting wall, indicating the
condition of construction is generally acceptable. However, the groundwater
leaked from the contact area between the foundation concrete of the collecting
wall and the bedrock (Fig. 6)
Fig. 6
Result of NPT-1 Test Pit Excavation
The NPT-2 test pit investigation was conducted at the corners of the water-
collecting wall in the left bank of the dam. The groundwater was flowing into the
1802
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik