the right side of the dam (together in the range of 200 L/s). The most important
perforated drills presented surge pressure of up to 7 Bars, it is estimated that the
anomalies found correspond to mostly vertical Tubular Karts, and permeably
connected with the rock stratification planes themselves with dips between 15 °
and 35 ° related to the vertical oriented downstream. The solution implemented
could not be equated to the first historical treatment due to the fact that there is a
full reservoir and the entrainment of the cementitious mixtures to the exterior (sites
downstream of the dam); nor could the unusual methods and materials of the
second historic treatment be used because on this occasion there was no suction
of the materials and the size of the filtration ducts intercepted by the perforations
were less than 2 inches. Finally, as one of the treatments, the injection of concretes
with maximum aggregate size of less than 1 inch was arranged, but the injection
with the traditional Trailer Pumps was detrimental to the geological environment
due to the fact that the "piston effect" [2] increased erosion deposits in the caverns;
therefore, for the solution, selected size aggregates were pushed without using a
concrete pump and intermittent mortar grout with smaller a size injection pump.
The sealing work on the left abutment had as a relevant factor, improving the
contact surface between the concrete masses of the dam and the foundation rock
with this treatment.
1. INTRODUCTION
El Cajón hydroelectric Project is located in the central zone of the Republic
of Honduras. The dam site is located on the Comayagua river basin about 2 Km
downstream from the junction of the Humuya and Sulaco rivers. The structure is a
double curvature thin concrete arch dam, of 226 m high.
The foundation of the dam site is located on cretaceous thick limestone rock,
the original construction had identified the presence of Karstic Phenomena located
in the inside and outside of the bathtub grounding curtain. During the life of the
project (around 33 years), the monitoring system has detected periodically
changes in the followings parameters: infiltration flow and uplift. These variations
have been attributed to process of dissolution and deposit erosion of such Karsts.
Over the past, few years one of the greatest anomalies was the increase in
the flow of the "D-1" drain of the drainage system, in the left abutment of the dam,
approximately between 106 and 135 m a.s.l. Initially in this drain, there was no
infiltration, later between the years 2006 to 2015 an increase of approximate 20 l/s
[3] was reported and some sediment drag (erosion). One of the tasks of the third
reinforcement campaign was to seal this infiltration.
1849
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik