The size of oscillation did not meet the IEC 60308 standard, and for this
reason, the power output test failed during the commissioning test and
substantial completion of the project was not achieved on time and got delayed
several times under this situation.
According to the IEC standard, the acceptable power swings on a hydro
generation unit should not be more than 5%(peak to peak) of the rated power,
but, the measured power swings on two of the three units in the Patrind plant
were approximately around 20%.
Fig. 2 Fig. 3
Active power output Governor position
2.2. CAUSE ANALYSIS OF POWER SWING
In Fig.3 above, the corresponding governor position is shown. It can be
clearly seen that the governor position shows no oscillation. Consequently, the
power oscillations are not expected to be caused by an insufficient control
algorithm or by the governor’s instabilities.
Since the severe power oscillations occur at high loads, we concentrate our
examination on the time region between 120 minutes and 150 minutes of the
measured data. In Fig.4 below, the governor position is plotted again but only in
the examined time region. Here again, it can be observed that the governor
position is nearly constant and cannot be the reason for the oscillations.
Fig. 4 Fig. 5
Governor position Active power output of threeunits
in the examined time region
2158
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik