absolute difference. Three operation points were calculated for the full model with
the intake and the operation of the two units in parallel.
The difference in efficiency is shown by means of green dots. For the
generator efficiency and other losses a constant value of etaGeno and other losses
= 98% was used to calculate the electrical power output based on the CFD data.
The CFD analysis correlates with the on-site measurement data and confirms the
findings established during the hydraulic structure model test [9]. Over the whole
operation range the measurement of turbine 1 shows a higher performance as
turbine 2. In relation to the generator output the relative losses are in the range of
7% at 20% flowrate and approx. 1.5% at 95% of the maximum flowrate (black
line). In terms of losses in relation to the maximum generator output the range is
between 1 and 2% (red line).
2.3. OPTIMISATION
Multiphase calculations were realised to verify the air sucking turbulences
and swirls. Based on the results of these simulations, different kinds of structural
measures were developed. The various types of measures were simple ac-
cessory elements as well as large-scale structural interventions at the inlet area
of the power plant. The effects of all these different structural adjustments on the
inflow were further investigated by means of computational fluid dynamics. The
inferior inflow situation is a fact, optimisation with additional guide walls and other
modification was analysed. 34 different variants were investigated, but with
simple elementary structures no substantial improvement could be realised. With
more complex and extensive guide walls also at the bottom of the intake a flow
distribution approximately comparable to turbine 1 could be realised. However,
with no option the Fisher-Franke [10] criteria are satisfied.
Fig. 4 shows the initial situation and 2 modifications. With the modification
of 3 guide walls a more homogeneous flow distribution could be realised (see
velocity distribution), and with the second modification presented even the swirl at
the bottom could be avoided (red streamlines). The velocity distribution presented
in absolute values at the right side of Fig. 4 also shows a flat gradient for version
(c), which indicates a smoother velocity distribution. Still, all these variants could
not satisfy the Fisher-Franke criteria or a comparable velocity distribution of
turbine 1. The operator of the power plant defined the possible frame conditions
with a few mandatory criteria. This includes the project costs, the operational
capability of the track rack cleaner, secure operation and massive construction of
the structures (e.g. guide wall made of steel) especially for flood water. A solution
without modifications of the pier made of concrete and other structures has to be
found in order to avoid the necessity of emptying the head water reservoir. The
best solution would be a massive guide wall made of steel (Fig. 4), which is a
modified and enhanced version of the principle idea presented in [9]) and a
modification of the pier made of concrete. These measures would incur expenses
more than 3 times higher as the given budget (calculated by the operator
including operation interruption).
2256
Book of Full Papers
Symposium Hydro Engineering
- Title
- Book of Full Papers
- Subtitle
- Symposium Hydro Engineering
- Author
- Gerald Zenz
- Publisher
- Verlag der Technischen Universität Graz
- Location
- Graz
- Date
- 2018
- Language
- English
- License
- CC BY-NC-ND 4.0
- ISBN
- 978-3-85125-620-8
- Size
- 20.9 x 29.6 cm
- Pages
- 2724
- Keywords
- Hydro, Engineering, Climate Changes
- Categories
- International
- Naturwissenschaften Physik
- Technik